Short Answer:
A differential protection scheme is a protective method used in power systems to detect internal faults in equipment like transformers, generators, and busbars. It works by comparing the current entering and leaving the protected section. If the difference between the two is more than a preset value, it indicates a fault inside the equipment.
This scheme is very sensitive and fast, providing accurate fault detection without being affected by external disturbances. Differential protection is widely used because it provides selective, reliable, and fast isolation of faulted equipment.
Detailed Explanation:
Differential protection scheme
The differential protection scheme is based on a simple but powerful principle: under normal conditions, the current entering a zone should be equal to the current leaving it. If there is a mismatch or “difference,” it signals that a fault has occurred within the protected zone. This zone could be a transformer, a generator, a transmission line, or a busbar.
The system uses Current Transformers (CTs) at both ends of the equipment to measure the currents. These values are compared in a relay. If the difference exceeds a set threshold (called differential current), the relay operates and sends a trip command to the breaker, isolating the fault.
Working principle of differential protection
- Current measurement:
- CTs are installed at both ends of the protected equipment (like a transformer).
- They measure incoming and outgoing current simultaneously.
- Comparison logic:
- The relay compares the two currents.
- Under normal operation and external faults, the difference is nearly zero.
- Fault detection:
- If a fault occurs inside the zone, current entering ≠ current leaving.
- This difference (differential current) exceeds the setting and the relay operates.
- Tripping action:
- The relay sends a signal to trip the circuit breakers at both ends to disconnect the faulty equipment immediately.
Types of differential protection
- Unit protection: Protects only the designated zone (e.g., a transformer).
- Percentage differential protection: Used in transformers to avoid false tripping due to CT errors or magnetizing current. It uses a slope or bias setting to account for such variations.
Applications of differential protection
- Transformer protection:
Detects internal winding short circuits or insulation failure. - Generator protection:
Detects rotor or stator faults which cannot be sensed by other relays. - Busbar protection:
Provides fast clearing of internal busbar faults. - Feeder protection (in some cases):
Used where high-speed fault clearing is needed on sensitive feeders.
Advantages of differential protection
- High sensitivity: Detects even small internal faults quickly.
- Selective: Does not trip during external faults.
- Fast operation: Ideal for critical equipment requiring quick disconnection.
- Reliable protection: Reduces the risk of equipment damage and system instability.
Limitations
- CT matching required: Any error in CT ratio or polarity can lead to unwanted operation.
- Expensive: Requires CTs and relays at both ends, increasing cost.
- Limited to specific zones: Cannot protect the full system; only localized areas.
Conclusion:
A differential protection scheme is a selective and fast-acting method used to protect vital power system components by detecting differences in current entering and leaving the equipment. It plays a critical role in preventing damage due to internal faults and ensuring system stability. With high accuracy and reliability, it remains one of the most effective protection techniques in modern power systems.