Why Power Plant Capacity Rated in MW and not in MVA?

November 17, 2017 by Dollar

DWQA Questions › Category: (EE) Power System › Why Power Plant Capacity Rated in MW and not in MVA?
0 Vote Up Vote Down
Dollar asked 6 years ago
3 Answers
0 Vote Up Vote Down
Bhisham answered 6 years ago

For the following reasons, a Power plant capacity rating may be expressed in MW instead of MVA.
In a Generating station, the prime mover (Turbine) generates only and only active power. That’s why we rated a power plant capacity in MW instead of MVA. Its mean no matter how large your generator is, but it depends on the capacity of the  engine (Prime mover/Turbine) I.e. a 50MW turbine connected to a 90MVA alternator in a power plant will generate only 50MW at full load. In short, a power plant rating is specified in terms of prime mover /Turbine (Turbine rating may be seen by nameplate rating which is in MW or Horsepower (HP) not in MVA) and not by the alternator set coupled to it.

0 Vote Up Vote Down
brno answered 6 years ago

MVA is the apparant power, MW is the real power and, MVAR is reactive power. MW describes the actual power that can be supplied to the load and MVA includes both the power supplied to the load AND the power that recirculates between the power plant and the load (volts*amps).
Watt : Is For Real Power
Real Power = apparent power * Power Factor (P.F)
And Power Plants have resistive Loads So it’s rated in MW.

0 Vote Up Vote Down
Rubi answered 6 years ago

MW describes the actual power that can be supplied to the load (voltsampscos theta).
MVA includes both the power supplied to the load AND the power that recirculates between the power plant and the load (volts*amps).
Because power plants have to supply both reactive and resistive loads, the two ratings describe a different capability. Most importantly, all of the power electronic devices, transformers, and switchgear in the system have to be sized against the MVA rating, not the MW rating. This is because reactive loads will cause currents to flow that circulate between phases (as opposed to active loads, which consume power from the utility) but don’t actually deliver active power to the load.

Primary Sidebar

Related Questions

  • What is real, reactive, and apparent power? asked by admin
  • Why HVDC line do not require any reactive power compensation? asked by admin
  • What is the Difference between blackout and brownout in power system? asked by
  • What are the different types of faults which occur in a power system? asked by admin

INTERVIEW QUESTIONS

MCQ or Objective


Recommended Post

MCQs on Transmission and Distribution

MCQ on Power electronics – 1

MCQ on Cables – 2

MCQs on Engineering Materials

MCQ on Measuring Instruments – 4

Categories



Join Our Whatsapp Group


About Us | Privacy Policy | Disclaimer


Copyright@ Since-2017