How to Calculate the suitable Capacitor size in Farads & kVAR for Power factor Improvement?

December 28, 2017 by Tilak

DWQA Questions › Category: (EE) Power System › How to Calculate the suitable Capacitor size in Farads & kVAR for Power factor Improvement?
0 Vote Up Vote Down
Tilak asked 3 years ago
3 Answers
0 Vote Up Vote Down
Varun answered 3 years ago

Motor input = P = 5 kW
Original P.F = Cosθ1 = 0.75
Final P.F = Cosθ2 = 0.90
θ1 = Cos-1 = (0.75) = 41°.41; Tan θ1 = Tan (41°.41) = 0.8819
θ2 = Cos-1 = (0.90) = 25°.84; Tan θ2 = Tan (25°.50) = 0.4843
Required Capacitor kVAR to improve P.F from 0.75 to 0.90
Required Capacitor kVAR = P (Tan θ1 – Tan θ2)
= 5kW (0.8819 – 0.4843)
= 1.99 kVAR
And Rating of Capacitors connected in each Phase
1.99/3 = 0.663 kVAR.

You are welcome to read more Important Interview Questions and MCQs.

0 Vote Up Vote Down
Berin answered 3 years ago

A 3 Phase, 5 kW Induction Motor has a P.F (Power factor) of 0.75 lagging. What size of Capacitor in kVAR is required to improve the P.F (Power Factor) to 0.90?
Motor input = P = 5 kW
Original P.F = Cosθ1 = 0.75
Final P.F = Cosθ2 = 0.90
θ1 = Cos-1 = (0.75) = 41°.41; Tan θ1 = Tan (41°.41) = 0.8819
θ2 = Cos-1 = (0.90) = 25°.84; Tan θ2 = Tan (25°.50) = 0.4843
Required Capacitor kVAR to improve P.F from 0.75 to 0.90
Required Capacitor kVAR = P (Tan θ1 – Tan θ2)
= 5kW (0.8819 – 0.4843)
= 1.99 kVAR
And Rating of Capacitors connected in each Phase
1.99/3 = 0.663 kVAR

0 Vote Up Vote Down
ravu answered 3 years ago

Step 1 – Calculate Actual Load (kW)
(Load) Power kW = Volts V x √3 x Current I x Power factor Pf
Step 2 – Calculate Required Power Factor Correction (kVAr)
Power Factor Correction kVAr = Power kW (TanΦi – TanΦd)
Φi = Cos-1 Initial Power Factor Pf
Φd = Cos-1 Required Power Factor Pf
Step 3 – Calculate Actual Power Factor Correction [kAVrl
Actual Power Factor Correction Pf = Cos (Tan-1 (TanΦi – Correction kVAr/Power kW ))
Typical Power Factor Correction available in multiples of 25kVAR’s, for further details please Contact Blakley Electrics Technical Department.

You are welcome to read more Important Interview Questions and MCQs.

Primary Sidebar

Related Questions

  • List of equipment in substation asked by
  • Why stones are used in switch yard ? asked by
  • List out the equipment used in a substation? asked by admin
  • What is load shedding? asked by

INTERVIEW QUESTIONS

MCQ or Objective





Recommended Post

MCQs on Engineering Materials

Basic Civil Engineering MCQ

Ohm Law

MCQs on Transformer

MCQ on Strength of Materials – 1

Categories

  • Electrical Articles (19)
  • Electrical MCQ (75)
  • Electrical Questions (11)
  • Interviews Questions (7)
  • IQ Test (1)
  • Uncategorized (10)

About Us | Privacy Policy | Disclaimer

Copyright@2017-2021