How to Calculate the suitable Capacitor size in Farads & kVAR for Power factor Improvement?

December 28, 2017 by Tilak

DWQA Questions › Category: (EE) Power System › How to Calculate the suitable Capacitor size in Farads & kVAR for Power factor Improvement?
0 Vote Up Vote Down
Tilak asked 6 years ago
3 Answers
0 Vote Up Vote Down
Varun answered 6 years ago

Motor input = P = 5 kW
Original P.F = Cosθ1 = 0.75
Final P.F = Cosθ2 = 0.90
θ1 = Cos-1 = (0.75) = 41°.41; Tan θ1 = Tan (41°.41) = 0.8819
θ2 = Cos-1 = (0.90) = 25°.84; Tan θ2 = Tan (25°.50) = 0.4843
Required Capacitor kVAR to improve P.F from 0.75 to 0.90
Required Capacitor kVAR = P (Tan θ1 – Tan θ2)
= 5kW (0.8819 – 0.4843)
= 1.99 kVAR
And Rating of Capacitors connected in each Phase
1.99/3 = 0.663 kVAR.

You are welcome to read more Important Interview Questions and MCQs.

0 Vote Up Vote Down
Berin answered 6 years ago

A 3 Phase, 5 kW Induction Motor has a P.F (Power factor) of 0.75 lagging. What size of Capacitor in kVAR is required to improve the P.F (Power Factor) to 0.90?
Motor input = P = 5 kW
Original P.F = Cosθ1 = 0.75
Final P.F = Cosθ2 = 0.90
θ1 = Cos-1 = (0.75) = 41°.41; Tan θ1 = Tan (41°.41) = 0.8819
θ2 = Cos-1 = (0.90) = 25°.84; Tan θ2 = Tan (25°.50) = 0.4843
Required Capacitor kVAR to improve P.F from 0.75 to 0.90
Required Capacitor kVAR = P (Tan θ1 – Tan θ2)
= 5kW (0.8819 – 0.4843)
= 1.99 kVAR
And Rating of Capacitors connected in each Phase
1.99/3 = 0.663 kVAR

0 Vote Up Vote Down
ravu answered 6 years ago

Step 1 – Calculate Actual Load (kW)
(Load) Power kW = Volts V x √3 x Current I x Power factor Pf
Step 2 – Calculate Required Power Factor Correction (kVAr)
Power Factor Correction kVAr = Power kW (TanΦi – TanΦd)
Φi = Cos-1 Initial Power Factor Pf
Φd = Cos-1 Required Power Factor Pf
Step 3 – Calculate Actual Power Factor Correction [kAVrl
Actual Power Factor Correction Pf = Cos (Tan-1 (TanΦi – Correction kVAr/Power kW ))
Typical Power Factor Correction available in multiples of 25kVAR’s, for further details please Contact Blakley Electrics Technical Department.

You are welcome to read more Important Interview Questions and MCQs.

Primary Sidebar

Related Questions

  • What will happen when power factor is leading in distribution of power? asked by
  • Can synchronous generator generates reactive power? asked by
  • List out the equipment used in a substation? asked by How Engineering Works
  • What is the role of link in neutral in a three phase ac system? asked by

INTERVIEW QUESTIONS

MCQ or Objective


Recommended Post

Ten important things about DC Motors or Direct Current Motor

Ten important things about DC Motors

EMF or Electromotive Force

MCQs on Electrical Circuit Theory

MCQs on DC motor

Categories



Join Our Whatsapp Group


About Us | Privacy Policy | Disclaimer


Copyright@ Since-2017